Het enige wat ik kan vinden in NFPA13:
8.14.2 Vertical Shafts.
8.14.2.1 General. Unless the requirements of 8.14.2.1.1 or 8.14.2.1.2 are met, one
sprinkler shall be installed at the top of shafts.
8.14.2.1.1 Noncombustible or limited-combustible, nonaccessible vertical duct shafts shall
not require sprinkler protection.
8.14.2.1.2 Noncombustible or limited-combustible, nonaccessible vertical electrical or
mechanical shafts shall not require sprinkler protection.
8.14.2.2* Shafts with Combustible Surfaces.
8.14.2.2.1 Where vertical shafts have combustible surfaces, one sprinkler shall be installed
at each alternate floor level.
8.14.2.2.2 Where a shaft having combustible surfaces is trapped, an additional sprinkler
shall be installed at the top of each trapped section.
Volgens mij moet je de warmte niet 'vangen' maar moet je onderliggende sprinklerkoppen beschermen tegen water van bovenliggende sprinklers omdat anders de kop niet geactiveerd wordt. Maar ik kan dat ff niet vinden in de NFPA